Bit twiddling

Doug-P

Member
Join Date
Jun 2003
Location
Pa
Posts
1,248
The recent thread(http://www.plctalk.net/qanda/showthread.php?t=43018) about finding adjacent ones piqued my interest. Is there an easier, faster way to do this than sequentially searching through every bit pair of interest?

After some experimentation I found something I think works fairly well. For test purposes I used three sixteen-bit words. The processor is a PLC-5

1. AND the two LSBs of the least significant word. Obviously, if both of these are ON the condition is met

2a. Make a copy of the argument(s)

2b. Right-shift the copy by one bit. This is easily done on A-B processors with the BSR instruction. In fact, if the words are contiguous, only one instruction is needed to shift dozens or hundreds of bits.

2c. AND the copy with the original argument into RESULT

2d. Test RESULT for a non-zero condition. This test can be done on individual words or a whole file. Any non-zero result word indicates that two adjacent bits are set.

If you're looking for zeroes you could NOT the argument before processing starts.

A caveat, make sure the bit shifted in to the BSR is always zero or you may get an erroneous hit.

Comments?
 
I don't see the savings...Whether indexing or Bit shifting, you are still 'moving' through the individual bits to check.
 
Bit hacks come up from time to time.

Log2 (X & (NOT(X-1)))

X & (NOT(X-1) gives you a number with only the least significant bit of X set.

Log base 2 of a binary number with only a single bit set will give you the position of that bit. There are several bit hacks online that will give you log2 withouth actually computing it (too busy to look it up myself).

This method would need to loop only once for every bit set, ie, if 7 bits are set then it will only need to loop 7 times.
 
Peter Nachtwey said:

Yes!!!

Actually, after re-reading Doug's solution I get it. I missread it that he was checking the two LSBs each time after a shift, not the entire word. Good solution.
 
Peter Nachtwey said:
there is an easier way
Peter, do you mean by this that there is an easier way than what I posted? If so, could you point me to it?
 
1 copy the 3 16 bit registers as you said.
2. shift one copy left, not right. This avoids having to check the first two LSBs. If there are exactly 48 bits it probably doesn't make a different.
3. And the two sets of registers together.
4. There is no need to scan through all the bits one at a time. All that is needed is to now that any bits are set after any AND.
One could just jump to the TwoAdjacentBitsFound lablel after finding the first non zero result after an AND.
 
My technical writing needs some work. What you describe is essentially what I was trying to get across.

Peter Nachtwey said:
1 copy the 3 16 bit registers as you said.
2. shift one copy left, not right. This avoids having to check the first two LSBs. If there are exactly 48 bits it probably doesn't make a different.
Yes, depending on the application the end bits probably won't matter. I only included this test for the sake of thoroughness.

Peter Nachtwey said:
3. And the two sets of registers together.
The heart of the thing.

Peter Nachtwey said:
4. There is no need to scan through all the bits one at a time. All that is needed is to now that any bits are set after any AND.
Here's where my explanation becomes less clear. It was not my intent to check every bit at this stage, hence step:

2d. Test RESULT for a non-zero condition. This test can be done on individual words (thereby checking sixteen bits at a time) or a whole file. Any non-zero result word indicates that two adjacent bits are set.

Peter Nachtwey said:
One could just jump to the TwoAdjacentBitsFound lablel after finding the first non zero result after an AND].
Yes. I'd do this with an FSC instruction. When the non-zero test is true the FD bit is set and appropriate action taken.

After thinking on it, the algorithm might be refined, that is, made faster, using a handmade loop rather than file instructions.

Regards
 
Doug-P said:
Yes. I'd do this with an FSC instruction. When the non-zero test is true the FD bit is set and appropriate action taken.

After thinking on it, the algorithm might be refined, that is, made faster, using a handmade loop rather than file instructions.
The file instructions execute in machine code whereas the ladder probably has some overhead and the loop certainly does. I would check the execution times before making that assumption.

I know this would execute quickly if written in S7's STL.
 

Similar Topics

See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot...
Replies
7
Views
283
A couple days ago I accidentally toggled an alwasyoff bit. The issue is it was set up as a single OTU on a rung, nothing else, and used as XICs...
Replies
3
Views
226
Hi I have an old panel builder 32 that I’m replacing for a factory talk me hmi . In the plc for the old panel builder there is a coms bit for the...
Replies
0
Views
74
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
Replies
1
Views
158
I tried researching but I still don't quite get it. As far as I understood, it's used after a function is called in STL and then if the function...
Replies
1
Views
143
Back