hi,
i was called in to help one of our customers with their PLC. it is a siemens which i'm not very familiar with. i typically work with GE fanuc or allen bradley. anyway, here is their setup:

main rack:
PS307 - power supply (120 vac)
CPU315-2DP - CPU
IM360 - interface module
SM321 - 24VDC DI (16 point) (there are 7 of these)

expansion rack:
IM361 - interface module (24VDC power)
SM331 - Thermocouple (8 point)
SM334 - 4 AI; 2 AO
SM322 - Relay DO (16 point) (there are 5 of these)

the 24VDC power was shorted out by accident and the unit stopped working. i checked the IM361 module PCB and saw it was smoked. replaced that and powered it on again. the SF LED turned on for both the IM360 and IM361. also, the CPU had all of it's LED's blinking simultaneously. i talked to the company's programming guy across the country and he said to replace the IM360 module and it should work. i also talked to siemens tech support and he said to replace the CPU and possibly the IM360. he said the blinking LED's on the CPU meant it was put into "panic mode". my customer is thrifty and i don't want to order an expensive new CPU if i don't need to. has anyone had something like this happen before or could offer any insight?
 
I had a cpu which had 120v connected to the 24v dc line (Thanks, boss). It fried an analogue card and stopped the cpu communicating with my programmer, but the processor still ran.
Try communicating with the processor. If you cannot, then the customer will have to get his cheque book out!!!
 

Similar Topics

Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,066
Hello all, Newbie in Siemens, I want to ask if there will be any issue when I download the instance datablock of a certain Function block? Also...
Replies
6
Views
4,413
hello, I'm new in automatics, and i'm working on a speed control project for a hydraulic turbine. i'm using FB41 pid bloc, but the LMN give me 0...
Replies
3
Views
2,259
Hi guys, Tomorrow I'm heading down to take a look at an existing SCADA system that has failed, and I was wondering if anyone had some suggestions...
Replies
18
Views
12,818
Hi Guys, I am facing a problem with my Siemens Simatic S7-300,CPU 315-2 DP( 6ES7315-2AF03-0AB0 ).That is in the morning i dont know why but it...
Replies
3
Views
3,349
Back
Top Bottom