panelview- ML1200

stu

Member
Join Date
Aug 2005
Location
England
Posts
783
Hi Guys, i am under the impression that you can connect the panelview to a mlx 1200 to view the tags when writing a program? can someone guide me in the right direction?thanks stu
 
STU, Please somebody corrects me if i´m wrong but the only way to program a ML1200 is offline, so I do not see how to do what you say. I have connected PV to ML1200, but both programs RSlogix 500 and panelbuilder have to be done offline and later download them to plc and pv respectively.
 
hi i have been told that using studio you can go into comms setup and create a link between mlx and pv.then you can view the tags on the plc while you are entering tags to buttons? not to sure myself so i am asking if anyone has done this before. thanks stu
 
Yes, you can online browse the MLX controller tags from FTView ME Studio. That is the programming software for the PanelView Plus.

PanelView Standard uses PanelBuilder32, and no it does not online browse tags.


See page 6-5 of the FT View Studio Machine Edition user manual for online tag browsing:
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/viewme-um004_-en-e.pdf

The other half of the manual.
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/viewme-um005_-en-e.pdf
 
hi i have set up the comms in comms set up (the short cut) it is seeing the df1 with the micrologix but when i go to tag browser it is seeing the shortcut there but when i click to view the tags there is nothing? any ideas thanks stu
 
If you are using FTView Studio 4.0 or earlier, then the MLX tags will not show up. The online browsing to the MLX was not supported until FTView Studio 5.0

However, you can enter the tag address in manually (where needed) and it will work. Or, install/use RSLinx Classic (free use with Studio) to do your online tag browsing.


Try the following two technotes from the Rockwell knowledgebase for workarounds:

MLX controllers do not show tag in FTView ME 4.0 or earlier
http://rockwellautomation.custhelp....ion.cfg/php/enduser/std_adp.php?p_faqid=33092

General information about tags not showing up
http://rockwellautomation.custhelp....ion.cfg/php/enduser/std_adp.php?p_faqid=33198
 

Similar Topics

I need to connect a 2711 k6c9 panelview to a ML1200 PLC. I do have a spare 1761 cbl pm02 cable. What do i need to do to this cable to get the...
Replies
3
Views
2,848
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
82
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
56
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
173
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
83
Back
Top Bottom