Hi

I can't upload the application from PanelView 1000 2711-T10C9, using RSLinx DF-1, the panel view is connected to SLC 5/03 via
DB9.

Can you help me with this
 
Its unclear how you are trying to upload the PV's program.
Tell us how you are connected to the PV (thru the SLC or connected directly to the PV?
Your PV supports DH485 protocol DF1 will not work unless you are trying to passthru the SLC.
We need more info.
 
Since your panelview uses DH485, you can't upload directly from the port as you have found.

You will have to use an alternate method, like the memory card.

If you have a 1747-PIC module you could use that as an interface, but there can be problems using it's driver with Windows XP SP3. If you have another method of connecting your PC to the DH485 network, then you can do it that way, (like the 1747-UIC).

If you can connect to the SLC channel 0 serial port, then you can clear bit S:34/6 to allow pass through, and then upload and download through the SLC serial port.

It really depends on what tools you have access to. The memory card is my favorite, and will work with all Panelview standard terminals except the 300 micro. It is also the fastest, and you can easily teach Joe the maintenance tech how to use it to replace a failed unit and get it up and running the quickest...

Paul
 
Last edited:

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
152
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
Replies
2
Views
228
Hi All, I was wondering if it is possible to use parameter files that can be passed to a second page eg: --HOME ---PUMP 1 FACEPLATE (With...
Replies
4
Views
1,153
Hi! I recently discovered how to get to configuration mode and disable printing for connecting to PanelBuilder32 and updating my Panelview...
Replies
1
Views
458
Last night electricians replaced the panelview and now there is no comms between the panelview and the PLC. The processor is a 1747-L541 SLC 5/04...
Replies
4
Views
914
Back
Top Bottom