Eric Nelson
Lifetime Supporting Member + Moderator
Hi guys! Yeah, it's been a (long) while, but I'm back!...
I've stayed in the industry, but haven't done much PLC work over the past few years. I just started getting back into machine building, but I'm way out of practice with my AB skills.
Here's the deal...
One of my customers has a labeler with a ML1200 running it. They are adding a feeder bowl to it which is controlled by a ML1000. I need to be able to adjust a handful of timers in the feeder bowl using the Maple Systems HMI on the labeler. I installed a 1761-NET-AIC on each of the PLCs. The AICs are connected to the PLCs via a 1761-CBL-AM00 cable (the one with the mini-DIN connectors on each end) on Port 2 of the AICs. The Maple Systems HMI is connected via RS-232 to Port 1 (the DB-9 connector) on the labeler. The two AICs are connected to each other via DH-485 (Port 3 to Port 3).
A diagram might clarify my setup:
The Maple Systems HMI currently communicates fine with the ML1500 with this setup, and I can connect to the ML1000 with my laptop thru Port 1 of the second AIC. The ML1200 does not have the secondary COM port.
Note: I do NOT need to talk directly to the ML1000 from the HMI, I only need to send a dozen or so integer values (N7:nn) from the ML1500 to the ML1000 (one way).
Now my questions:
The HMI is currently connected using DF1 thru the AIC's serial port. Will I have to move it to the DH-485 network?...
What settings do I have to change on the PLCs? I haven't played around with it much yet. I did try changing the ML1000 to node 2, but of course I immediately lost comms. with it...
I still have both PLCs set to DF1 Full Duplex. I assume I'll need to change them both to DH485, or does the AIC do that for me?...
Sorry for what are probably newbie questions, but I haven't touched any AB stuff in the past 10 years or so...
Let me know if I need to clarify anything!
-Eric
I've stayed in the industry, but haven't done much PLC work over the past few years. I just started getting back into machine building, but I'm way out of practice with my AB skills.
Here's the deal...
One of my customers has a labeler with a ML1200 running it. They are adding a feeder bowl to it which is controlled by a ML1000. I need to be able to adjust a handful of timers in the feeder bowl using the Maple Systems HMI on the labeler. I installed a 1761-NET-AIC on each of the PLCs. The AICs are connected to the PLCs via a 1761-CBL-AM00 cable (the one with the mini-DIN connectors on each end) on Port 2 of the AICs. The Maple Systems HMI is connected via RS-232 to Port 1 (the DB-9 connector) on the labeler. The two AICs are connected to each other via DH-485 (Port 3 to Port 3).
A diagram might clarify my setup:
LABELER FEEDER BOWL
+-----------+ +-----------+
ML1500<---->|(2) AIC (3)|<------DH-485------>|(3) AIC (2)|<----> ML1200
| | | |
| (1) | | (1) |
+-----------+ +-----------+
^
|
Maple HMI<--------+
The Maple Systems HMI currently communicates fine with the ML1500 with this setup, and I can connect to the ML1000 with my laptop thru Port 1 of the second AIC. The ML1200 does not have the secondary COM port.
Note: I do NOT need to talk directly to the ML1000 from the HMI, I only need to send a dozen or so integer values (N7:nn) from the ML1500 to the ML1000 (one way).
Now my questions:
The HMI is currently connected using DF1 thru the AIC's serial port. Will I have to move it to the DH-485 network?...
What settings do I have to change on the PLCs? I haven't played around with it much yet. I did try changing the ML1000 to node 2, but of course I immediately lost comms. with it...
I still have both PLCs set to DF1 Full Duplex. I assume I'll need to change them both to DH485, or does the AIC do that for me?...
Sorry for what are probably newbie questions, but I haven't touched any AB stuff in the past 10 years or so...
Let me know if I need to clarify anything!
-Eric