I hope this best described my situation.....What i am trying to do in the sample attached is that when a bit is true an initial value is mov into (o:i.5) but if one of the condition we set come through (i.e B3:8/0 on rung 0001 not 7 my mistake)and the force is less than 15000 add 100 and replace (O:1.5) with with the new value , which will make it our new number. For example if b3:8/0 comes through add 100 to initial setting and the new number will be 15100. By the way i am using micrologix 1100. Hope this helps
Well, that is somewhat less vague, however, your first and second examples are completely different.
Based on your second example, if B8/0 comes true and O:1.5 is less than 15000 for 20 ms (Did you really want that short of a delay?) you will add the current value in N7:6 to O:1.5 for one scan because of the one shot.
However, if B7/0 is still true O:1.5 will go back to 15000 on the next scan. If it is not true, then O:1.5 will go to zero, because there is nothing updating it.
Also in Rung 2, when T4:13 is not done, you will be adding 100 to N7:6 every scan until the timer is done, or you overlflow N7:6 (Maximum 32,767).