Level transmitter input averaging

jschwalb

Member
Join Date
Jun 2009
Location
Houston
Posts
2
Running 90-70's with cimplicity 6.1 and machine ed. 5.5.
Have two LT's in one tank and need a way to average the 2 in plc logic to show as bar graph on cimplicity project screen.
Any ideas?
 
If you're going to do as danw suggested, you should first convert the analog inputs to REAL or DINT variables. The raw data range in the %AI variables could be big enough that when you add two together, the result is greater than +32767, in which case you'll get an incorrect result if you add INT variables.
 
Thanks,

I'll post my solution when I'm finished, I have to account for any one of the 2 LT's not giving a value due to low volume and rig list.
 