fail safe mode in level transmitter works
Sabarish
May 2023
Singapore
How fail safe mode in level transmitter works? customer requesting for fail safe mode when the transmitter got any issue or power loss on the transmitter
Here's what Siemens says for one of their radar level transmitters:
The an offscale low or offscale high level is likely to trip alarms, which is one means of knowing that measurement is invalid. Whether high of low depends on what happens, whether pumps turn or off.
Holding at the last value might not alert anyone to the failure condition.
so how to differentiate the outputs , i mean if the high level triggers also get the same output and the fail safe also will get the same , how to differentiate these two output?iam using the FTL62 level switch from E&H,Kindly reply ,i dont have any idea about this fail safe attached the link with this https://bdih-prod-assetcentralapi-a...500261EDB89B75B40D436B0BA/TI01539FEN_0220.pdf
"Fail" states are normally configured above and/or below Hi and Lo states. It makes little sense to make them equivalent.
If the signal is within the normal 4-20mA range, then high and low level alarms are valid.
If it's less than 3.8mA or greater than 20.5mA then signal a sensor fault.
I use the sensor fault bit to mask the level alarms, so the operator only gets a "sensor fault" and not an additional level alarm.
To do that your delay on the level alarm needs to be longer than the delay on the sensor fault alarm.
Typically if I'm seeing a faulty sensor then all equipment that operates from that sensor either needs to to stop, or switch to some form of alternative or backup control method
what is meant by fail-safe mode of sensor. how to program when this sensor goes ON. usually i put a NO contact for the sensor and connect to...
2,853
After updating TIA selection tool I was notified that my PLC was now under "predecessor". It was not valid if the "fail-safe" operation was...
1,964
My employer is in the habit of applying a roller limit switch on a P&F chain overload in a non-fail-safe manner. The LS is only operated if the...
1,362
I read the WinMOD manual that simulate fail-safe IO is possible with A756. But actual not, here is my configuration, anyone successes with...
1,518
Hi guys.Can somebody explain me or give me a practical example what is the fail-safe technology/signals . For what i read it is force plant into...
2,570