Quantum - Sy/Max Traffic Cop

boydkiefer

Member
Join Date
Jul 2009
Location
Newark, NY
Posts
1
I am trying to add a Class 8030 RIM 127 (analog input RTD) module into a slot of a Sy/Max rack that is being used as remote I/O to a Modicon Quantum. When I try editing on traffic cop to "load" the module into slot #2 all the existing modules get a red "X" posted on them. I can't clear these X's away unless I remove (edit) the RIM 127 from the slot.
please help
 
Could be a problem with the version of card. I had a similar problem with the RIM121 module, series D worked fine but a series F card would go red (as yours does). If you are using Concept Schneider tech support should be able to help with a 'Modconnect' (I think) file. If you are using Unity you are probably out of luck. In either case you should talk to Tech support.
 

Similar Topics

Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
261
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
Replies
3
Views
652
Hey guys. Mostly new to this stuff so I apologize if I'm not following proper format. I have 3 working CPU133 /3s. There is a desktop with a...
Replies
2
Views
893
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
Replies
0
Views
496
Main rack contained power supply 140cps52400 and 140cpu43412A and RIO HEAD 140CRP93100 in addition to another I/o cards . Another remote rack...
Replies
8
Views
1,861
Back
Top Bottom