Has anyone networked CPM1A to a C200HE-CPU42-ZE processor? I need to replace 14 Omron C20 plc's that are starting to fail and would like to use CPM1A's with a CIF-11 comms module connected to a COM-06 on the C200HE. Is this possible and can I share data between the PLC's?

I have linked the C200HE to other devices using modbus but the smaller Omrons do not support modbus.
 
NO worries at all use the rs422 with a cif unit per plc.
Don't forget the terminator.
If you ar in melbourne look up Industrial Automation Products
(sorry about the add.)
It works
 
Last edited:
The hardware that you suggest is fine. Now comes the software part:

1. Each CPM1A will need a separate unit number assigned in PC Setup from 0-31.

2. The C200HE will need to use on of the following:
a. TXD-RXD instructions to poll the CPM1A's using Hostlink commands.
b. The COM06 board supports protocol macro commands. If you have the software, I will post the necessary protocol macro to accomplish this. :cool:
 
Thank you Ian and Jay for your replies.

I will purchase the protocol macro software and would like to take you up on your offer, Jay.

Paul
 
Here is the macro for C Mode Hostlink protocol. The .psw is for CX Protocol and the .pt1 is for Protocol Macro Software for DOS. Also is included the documentation. :nodi:
 

Similar Topics

I've got an upload from an Omron SYSMAC CPM1A PLC but I cannot figure out for the life of me how to document the inputs and outputs. It's version...
Replies
9
Views
3,267
Hi, I have recently purchased an old Omron Cpm1a plc to practice on. I have a version of syswin that does not require a licence to program these...
Replies
2
Views
1,661
I have a Omron PLC with CPM1A-MAD01 anaolog input output module its reading pt100 temperature probe. When the machine is running it starts to...
Replies
0
Views
1,089
Hi, I have recently being using a Omron CPM1A-40CDR-D-V1 and transferred an old program on it. I was testing the program and making some...
Replies
2
Views
4,243
I have two of the same units that are using a CPM1A and an NT20S-ST121B-EV3. I am not able to connect to the touch screen as far as i can tell via...
Replies
16
Views
3,997
Back
Top Bottom