locotumbler
Member
OP
finally got back around to this issue. Turns out that at some point the plc lost all of its settings. i was able to manual set the values for the DM10 and DM11 which were the cycles until pause setpoints. I got two of the three machines working flawlessly. now i have an issue with one of them that if I power it up with the HMI connected it will kick it out of run mode. If i power it up with the HMI disconnected it will go into run mode and if I then connect the HMI after about 15-30 seconds it stays in run mode and runs without issue. have any of your Omron Guru's ever seen something like this?