If you need large amount of data fast, then you should be using Prosoft card
But if you want to read just a few words per second, then application works just fine.
Application distributed since 2004 under
C:\RSLogix 5000\Projects\Samples\ENU\v<xx>\Rockwell Automation
(replace <xx> with your version)
The secret to sucsess: do not try to modify any application code
Take a look at TN 32662 (Techconnect access level)
TN has an updated application that corrects most of the problems found in the intial version that was included with all previous versions of Logix
If you use
unmodified application, then no debugging needed and I strongly recommend you not to modify any code
For slave you will need to configure only address - nothing else needed - it will resond to master requests
For master - you will need to configure tags to set your master requests
You can monitor these requests using hyperterminal or WinHexCom.
And if you still believe that modification is necessary then let me know before you do it.