Hi
I've been thinking o_O about communicating a SLC 5/03 to a Contrologix L61. The L61 has a 1756-DHRIO and 1756-ENBT besides the DF1 port on the Controller. I need to write and read data back and forth on both devices. The L61 is conected to the DCS using a Prosoft Modbus board.

My question is: Is it possible to use the port DF1 on the controllers? Can the port on the L61 be set to talk to the 5/03 using DH485?

Since I've a 1756-ENBT I might use it as programming interface, but if successfull, will it allow me to enter the 5/03 though the L61 port?

Thanks.
 
The DHRIO module won't help, but a 1756-DH485 module would allow you to connect to the 5/03 DH485 port.

Alternatively, you could use plain old serial DF1 if the devices are within 50ft of each other.

Or, you could use the Logix serial port to a NET-AIC module connected to a DH485 port on the 5/03. Set the serial port for DH485, and give it a node number unique to the DH485 network. Then you can MSG to the 5/03 from the Logix CPU. This might make using the serial port for programming a bit of a PITA.

Another alternative might be to put a 1761-NET-ENI on the 5/03 serial port and connect it to the ethernet network with the ENBT module. Then you should be able to access both PLCs from ethernet and message between them.
 

Similar Topics

Hello, I have a problem and certainly just one of many to come as I become more involved with PLCs We've got a panelview 1000 connected to a SLC...
Replies
3
Views
3,189
Hello, can someone share/explain How to check comms between PC and PLC via TeamViewer? TIA
Replies
14
Views
426
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
323
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
Replies
8
Views
950
Hi, Does anybody have experience with Ethernet/IP-CIP Safety comms between 2 different brands of PLC's I have a project with 1 Safety Allen...
Replies
13
Views
3,607
Back
Top Bottom