protrac231 Member P Join Date Dec 2009 Location tampa Posts 19 Mar 1, 2010 #1 Does anyone know if I pull the prosoft module out to change a dipswitch setting, if I will fault the PLC processor?
Does anyone know if I pull the prosoft module out to change a dipswitch setting, if I will fault the PLC processor?
scalelar Member S Join Date Aug 2006 Location SE Tn Posts 62 Mar 1, 2010 #2 Right click on the module in the IO tree and select properties. On the connections tab if the "Major fault on controller if connection fails while in run mode" box is not checked you should be ok.
Right click on the module in the IO tree and select properties. On the connections tab if the "Major fault on controller if connection fails while in run mode" box is not checked you should be ok.