I have hardware as Micrologic 1500(12DI+12DO)+
Module1(6DI+4DO)+Module2(4AI)+Module3(2AO) we have interfaced this with PanelView C600 HMI, we are able to configure the I/O's on the basic ML1500 but other additional I/O's on Module1,2 & 3 are not able to be configured in HMI.The tag addresses assigned for the slot(0)ML1500 is I:0/0,I:0/1 and so on which are correctly displayed,similary we assigned tags for other module as I:1/0,I:1/1 etc but they are not able to be displayed on the I/O status page created on HMI even I tried to configure these Inputs as I:1.0,I:1.1 and so on, kindly someone plz guide me how to assign these additional I/O's into PanelView C600 HMI, I am very much new to the AB PLC systems.......Thanx
Module1(6DI+4DO)+Module2(4AI)+Module3(2AO) we have interfaced this with PanelView C600 HMI, we are able to configure the I/O's on the basic ML1500 but other additional I/O's on Module1,2 & 3 are not able to be configured in HMI.The tag addresses assigned for the slot(0)ML1500 is I:0/0,I:0/1 and so on which are correctly displayed,similary we assigned tags for other module as I:1/0,I:1/1 etc but they are not able to be displayed on the I/O status page created on HMI even I tried to configure these Inputs as I:1.0,I:1.1 and so on, kindly someone plz guide me how to assign these additional I/O's into PanelView C600 HMI, I am very much new to the AB PLC systems.......Thanx