Can anyone help me out with proper connection scheme?

I have the COM terminals on the input card connected to -24VDC, voltage supply to sensor connected to +24VDC. Sensor "-" is connected to "input 0-", sensor SIG is connected to "input 0+". Raw data is -704, regardless of applied pressure.

Sensor, BTW, is a Prosense , 0-100 PSI.
 
Have you changed the module to read voltage instead of current? I believe the factory default on those is current. Check out pub 1762-IN012A-EN-P
 
Have you changed the module to read voltage instead of current? I believe the factory default on those is current. Check out pub 1762-IN012A-EN-P

Yes, DIP switches are set to "voltage". You're right, though, they're factory-set to "current"
 
Can anyone help me out with proper connection scheme?

I have the COM terminals on the input card connected to -24VDC, voltage supply to sensor connected to +24VDC. Sensor "-" is connected to "input 0-", sensor SIG is connected to "input 0+". Raw data is -704, regardless of applied pressure.

Sensor, BTW, is a Prosense , 0-100 PSI.

If you are using Voltage, I don't imagine your Prosense is a 2 Wire Device. Can you supply the exact Prosense Model, or better yet post a link to the manual? My guess is you need to connect your Input 0- to -24VDC to Power the Sensor. I would like to see the exact Sensor setup though. Can you post a Screen Shot of your Configuration?

Stu.....
 
Last edited:
If you are using Voltage, I don't imagine your Prosense is a 2 Wire Device. Can you supply the exact Prosense Model, or better yet post a link to the manual? My guess is you need to connect your Input 0- to -24VDC to Power the Sensor. I would like to see the exact Sensor setup though. Can you post a Screen Shot of your Configuration?

Stu.....

No, as I explained, power supply to sensor is +24VDC, SIG is connected to Input 0+, COM is -24VDC.

Here's the link to sensor: http://www.automationdirect.com/adc..._Sensors/Pressure_Transmitters/PTD25-10-0100H
 
Based on the wiring diagram for that input card and sensor you should run pin 1 (L+) to 24V+, pin 2 to IN0+, and pin 3 (L-) to 24V-. 24V- also needs to run to IN0-. There shouldn't be anything wired to COM.
 
Based on the wiring diagram for that input card and sensor you should run pin 1 (L+) to 24V+, pin 2 to IN0+, and pin 3 (L-) to 24V-. 24V- also needs to run to IN0-. There shouldn't be anything wired to COM.

Thanks. I'll check it out it the morning.
 

Similar Topics

Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
Replies
0
Views
123
Hello, I am very new to the plcs and am working on a project that requires a fixed mount barcode scanner to scan packages as they move along a...
Replies
1
Views
210
Good afternoon, This one may sound crazy. I have a device that is configured to outputs a 0 to 10 volt signal. the scaling is 0 - 0 and 10 -...
Replies
4
Views
1,662
Dear All, 3 phases (380-400 volt) are needed for my small lap in my garage. Normally there is one 1 phase 220-230 volt in my garage but I would...
Replies
31
Views
6,871
We are installing 20 foot direct burial fiberglass light poles, and we are mounting speakers for a pa system on the pole about 12 feet up. Can the...
Replies
4
Views
1,834
Back
Top Bottom