Good afternoon,


This one may sound crazy. I have a device that is configured to outputs a 0 to 10 volt signal. the scaling is 0 - 0 and 10 - 200. well some times it can go above 200 into the 240 range or higher at this point. this will make the unit output 11 volts. this will make the unit that is connected to it fail. how can i clamp the 10 volts meaning i do not want it to go over 10 volt. Would a zener diode work.
 
Can you limit value to 10..200 on program before AO-output?


10V Zener would work put it won't correct original problem before AO output.
 
As you have discovered, scaling does not necessarily perform limiting/clamping. I'm not sure what PLC equipment you are using, but some Rockwell output modules have an Output Clamp feature.

OG
 
As you have discovered, scaling does not necessarily perform limiting/clamping. I'm not sure what PLC equipment you are using, but some Rockwell output modules have an Output Clamp feature.

OG

And a "Limit" instruction. (LIM) for AB PLC's
or roll your own.
 
Last edited:

Similar Topics

Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
Replies
0
Views
104
Hello, I am very new to the plcs and am working on a project that requires a fixed mount barcode scanner to scan packages as they move along a...
Replies
1
Views
200
Dear All, 3 phases (380-400 volt) are needed for my small lap in my garage. Normally there is one 1 phase 220-230 volt in my garage but I would...
Replies
31
Views
6,564
We are installing 20 foot direct burial fiberglass light poles, and we are mounting speakers for a pa system on the pole about 12 feet up. Can the...
Replies
4
Views
1,820
I had a conversation a while back with the Product Manager of the Productivity PLC I was asking for a CPU for the Productivity 1000 Series that...
Replies
26
Views
7,801
Back
Top Bottom