whew thanks for that Ron. The plant is shut down at the moment so I didn't notice. Have loaded the original program back onto the processor. I have followed all the steps you have outlined above and still no joy. The dip switches are all correct, S:16 is set for 11, the 'blue hose' is in the correct slot, and I tried to auto configure in Prog mode and it comes up with 'AutoConfigure completed successfully but remote I/O rack(s) possibly overlap local I/O rack(s)'. Nothing came up in the 'spreadsheet' and still didn't seem to be communicating so swapped the blue and clear wires around at 1 end and auto configured and it came up with 'AutoConfigure not successful - make sure I/O status file exists'. We do have other RIO hardware on plant so will try them to check the channel and ASB module, tomorrow. The ASB module is series E