camaroblk68

Member
Join Date
Jan 2008
Location
florida
Posts
2
I have to install a ethernet card on an S7 with a ET200M remote rack and i want to knowe if i can install the card (e-net) in the ET200M group? or does it need to be connected with the S7 prosecer?
 
I assume that you are talking about installing a CP 343 module. You can install it in an ET200m rack with no problems.

You probably have some type of IM-153 as the connection point to the main rack. The number of slots available in the rack are dependent on this module.

Also, if installing in a sub rack with an IM, you will be limited by the total number of bytes to that rack. All comms to the CPU need to pass through the IM.
 
I have to install a ethernet card on an S7 with a ET200M remote rack and i want to knowe if i can install the card (e-net) in the ET200M group? or does it need to be connected with the S7 prosecer?

AFAIK an CP343 doesn't work in a ET200M group. The CP343 should be in the rack where the CPU is, or in a extension rack (IM360/361).
 
Some definitions might be in its place here.

S7-300 modules in expansion-racks connected to the CPU rack via IM360+IM361:

A CP343-1 or any other specialty module that connects via the K-bus (MPI) on the backplane will work OK.

S7-300 modules in expansion-racks connected to the CPU rack via IM365.
or
S7-300 modules in expansion-racks connected to the CPU rack via IM153-1 or IM153-2 or IM153-3 (This is ET200M via DP).
or
S7-300 modules in expansion-racks connected to the CPU rack via IM153-4 (This is ET200M via PN):

A CP343-1 or any other specialty module that connects via the K-bus (MPI) on the backplane will not work. Some CPs that exchange data via the P-bus will work OK, such as CP340.
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
50
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
110
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
285
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
99
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
196
Back
Top Bottom