Siemens S7

camaroblk68

Member
Join Date
Jan 2008
Location
florida
Posts
2
I have to install a ethernet card on an S7 with a ET200M remote rack and i want to knowe if i can install the card (e-net) in the ET200M group? or does it need to be connected with the S7 prosecer?
 
I assume that you are talking about installing a CP 343 module. You can install it in an ET200m rack with no problems.

You probably have some type of IM-153 as the connection point to the main rack. The number of slots available in the rack are dependent on this module.

Also, if installing in a sub rack with an IM, you will be limited by the total number of bytes to that rack. All comms to the CPU need to pass through the IM.
 
I have to install a ethernet card on an S7 with a ET200M remote rack and i want to knowe if i can install the card (e-net) in the ET200M group? or does it need to be connected with the S7 prosecer?

AFAIK an CP343 doesn't work in a ET200M group. The CP343 should be in the rack where the CPU is, or in a extension rack (IM360/361).
 
Some definitions might be in its place here.

S7-300 modules in expansion-racks connected to the CPU rack via IM360+IM361:

A CP343-1 or any other specialty module that connects via the K-bus (MPI) on the backplane will work OK.

S7-300 modules in expansion-racks connected to the CPU rack via IM365.
or
S7-300 modules in expansion-racks connected to the CPU rack via IM153-1 or IM153-2 or IM153-3 (This is ET200M via DP).
or
S7-300 modules in expansion-racks connected to the CPU rack via IM153-4 (This is ET200M via PN):

A CP343-1 or any other specialty module that connects via the K-bus (MPI) on the backplane will not work. Some CPs that exchange data via the P-bus will work OK, such as CP340.
 

Similar Topics

Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
2
Views
97
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
9
Views
292
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
105
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
159
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
197
Back
Top Bottom