Siemens S7
camaroblk68
Jan 2008
florida
I have to install a ethernet card on an S7 with a ET200M remote rack and i want to knowe if i can install the card (e-net) in the ET200M group? or does it need to be connected with the S7 prosecer?
I assume that you are talking about installing a CP 343 module. You can install it in an ET200m rack with no problems.
You probably have some type of IM-153 as the connection point to the main rack. The number of slots available in the rack are dependent on this module.
Also, if installing in a sub rack with an IM, you will be limited by the total number of bytes to that rack. All comms to the CPU need to pass through the IM.
AFAIK an CP343 doesn't work in a ET200M group. The CP343 should be in the rack where the CPU is, or in a extension rack (IM360/361).
Some definitions might be in its place here.
S7-300 modules in expansion-racks connected to the CPU rack via IM360+IM361:
A CP343-1 or any other specialty module that connects via the K-bus (MPI) on the backplane will work OK.
S7-300 modules in expansion-racks connected to the CPU rack via IM365.
or
S7-300 modules in expansion-racks connected to the CPU rack via IM153-1 or IM153-2 or IM153-3 (This is ET200M via DP).
or
S7-300 modules in expansion-racks connected to the CPU rack via IM153-4 (This is ET200M via PN):
A CP343-1 or any other specialty module that connects via the K-bus (MPI) on the backplane will not work. Some CPs that exchange data via the P-bus will work OK, such as CP340.
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
91
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
284
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
103
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
159
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
197