PLC-5 LED's

ceilingwalker

Lifetime Supporting Member
Join Date
Mar 2010
Location
Phoenix, AZ
Posts
1,586
Good day all. I wanted to know if the LED's on the front of a a 1771-ID should light up for a specific terminal, if the proper voltage is put across it. I know on the SLC500 Input module whether it is programmed or not, if it sees 110V, it will light. I have three inputs that have 120V and the LED's are not lit. Other LED's on the same module are lit, with the same voltage. Also, please, how do I check IO configuration on a PLC-5? The IO config doesn't give a nice little list of the components, like the SLC500. Thank you.
 
Good day all. I wanted to know if the LED's on the front of a a 1771-ID should light up for a specific terminal, if the proper voltage is put across it. I know on the SLC500 Input module whether it is programmed or not, if it sees 110V, it will light. I have three inputs that have 120V and the LED's are not lit. Other LED's on the same module are lit, with the same voltage. Also, please, how do I check IO configuration on a PLC-5? The IO config doesn't give a nice little list of the components, like the SLC500. Thank you.

The 1771-ID is an Isolated Input Card, and has a seperate Neutral (L2) Connection for each Input on the even Terminals. Are these connected for each Input?

http://literature.rockwellautomation.com/idc/groups/literature/documents/td/1771-td019_-en-p.pdf

Stu....
 

Similar Topics

On this project, the operator's asked me to add an LED onto the cabinet of the PLC enclosure, such that the LED illuminates when the PLC's...
Replies
13
Views
1,047
Hi, I have an ABB AC500 PM-582 PLC, The question is... is it possible to get the compiled code out of the CPU, i need to have this as a backup...
Replies
7
Views
1,475
hi everyone i have this simple program using HSC i set the NEW_RV to 1000 when rotating the encoder and when reaching 1000 the counting restart...
Replies
3
Views
1,572
My boss has come up with the idea of renting machines and charging on a per use / per hour basis, so I'm looking into it - just getting my feet...
Replies
14
Views
3,977
Hi In one of our machine, there is Seimens PLC IM151-8 PN/Dp CPU. HMI is connected via Ethernet and other devices are connected via Profibus...
Replies
5
Views
3,123
Back
Top Bottom