PLC Shutting Down.

thetech

Member
Join Date
Jun 2010
Location
Louisiana
Posts
18
I'm working with a Automation Direct (P3-550) - 16in - 16 out. I have a input that sends an output to a relay to turn on a Operator Interface (Red Lion). The problem is when the Operator Interface tries to turn on the PLC shuts down and does a reboot. I'm using a good 10amp 24volt power supply, so lack of power is not the problem. What I did to fix it was put a capacitor across the P3-550 power supply inputs and the problem went away.

My question is what should be the correct value of capacitor should I use?

And is this the right step to fix this problem?

Thanks
TheTech


progress.gif
 
A reaonably good power supply should have capacity to avoid such. You may want to review the supply connections as you may have a voltage drop at some point. you don't want to daisy chain the supplies, rather bring them seperately off the supply for each device.
 
I do have the PLC and the Operator Interface daisy chained. But I figured with #14 wire and 10amp supply I would not have any trouble. I ques I was wrong. I'll run a [FONT=&quot]separate wire for each.

Thanks for the tip.

That was really quick.


[/FONT]
 
Another thing to remember is that while 14 ga Cu will handle 15 amp at 120 vac, you need to derate it by at least 50 % to 7 amps at 12 vdc...and over kill on the main power wiring can go a long way to 'fix' design boo-boo's...:mad:
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
4
Views
36
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
Replies
5
Views
114
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
29
Hi All, Someone at work has put a PLC system on my desk, that's just been taken off an idle production line. He said "It's an S7 PLC. We don't...
Replies
10
Views
189
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
55
Back
Top Bottom