Kind of interesting, we had half a dozen 120V circuits in our factory short out and start tripping their breakers.
First one went, and we assumed that someone drilled through the conduits under the concrete while mounting a machine to the ground. So we replaced the circuit and away it goes. Then 2-3 weeks later the rest shorted out, and we pulled out the circuits, the wires were completely black, and the insulation gone. And it was hot. The first one was hot too, but not very, we assumed the short circuiting had heated up the wires.
Scratching our heads, we tried to find out what caused it. Turns out there was an oven (no floor, just walls on top of the concrete with a natural gas burner) sitting right on top of where the conduits for these circuits travelled. The oven runs at 395F almost 24/7. THHN is rated for 190F.
So, the heat from the oven melted the insulation of the wires inside the underground conduit. I check out the ratings of various wires, but it seems that everything rated for 390+F is also for dry locations only, and I'm pretty sure buried under concrete counts as a wet location in the code book.
Anyone know of a wire rated for high temp and wet locations? Or am I just going to have to run the circuits through a new conduit running up to the ceiling instead of the ground?
First one went, and we assumed that someone drilled through the conduits under the concrete while mounting a machine to the ground. So we replaced the circuit and away it goes. Then 2-3 weeks later the rest shorted out, and we pulled out the circuits, the wires were completely black, and the insulation gone. And it was hot. The first one was hot too, but not very, we assumed the short circuiting had heated up the wires.
Scratching our heads, we tried to find out what caused it. Turns out there was an oven (no floor, just walls on top of the concrete with a natural gas burner) sitting right on top of where the conduits for these circuits travelled. The oven runs at 395F almost 24/7. THHN is rated for 190F.
So, the heat from the oven melted the insulation of the wires inside the underground conduit. I check out the ratings of various wires, but it seems that everything rated for 390+F is also for dry locations only, and I'm pretty sure buried under concrete counts as a wet location in the code book.
Anyone know of a wire rated for high temp and wet locations? Or am I just going to have to run the circuits through a new conduit running up to the ceiling instead of the ground?