oven temp control with two controllers in series
unsaint33
Sep 2019
MInnesota
118
We have a small plastic parts oven (SP at 210F). It used to have an old bimetal temperature regulator. We are upgrading it using two temperature controllers. Watlow EZ-Zone with mechanical relay outputs. One for regular SP control, the other for the high limit. The output contacts of these two controllers will be wired in series. Here is my question.... For the high limit controller, should I configure it with the heating mode and use the normally open contact? or the cooling mode and use the normally closed contact?
I don't have my references available, but I thought the EZ Zone controller could be configured as a Limit controller to do exactly as you wish. In that case, you would configure the first unit as heating mode (P, PI or PID) and the second unit as limit mode. You then set the alarm level and the output. It has been a while, so I apologize in advance if my thoughts are not correct.
I'm not an oven control expert, but I've worked around a few over the years. In my experience, the high limit controls do more than just block the addition of heat. They also drop and disable the automatic cycle of the system. It sounds like your system is a lot simpler than all of that.
That being said, I would set the output of the limit controller such that it fails safe. In other words, it needs to be powered on and healthy as well as the temperature being safe to allow the system to run.I would design the system such that it takes operator intervention to resume heating if the high limit control ever detects a high temperature condition.
Hi Joseph,
I am a plant electrician. We don't have an electrical engineer so I am tasked to make a simple design for this small oven.
A newbie question for you. I can set up one of my EZ-Zone controllers with an alarm function that de-energize the output and latches it off. Why do I need a high limit controller? Is that for safety redundancy?
Thanks for the clarification on the temp controllers vs limit controllers. I don't have my references handy. Sorry about misleading you.
Joseph - good call on the fail-safe wiring. That is important.
Regarding the use of limit controllers, it is a good idea to have the limit controllers for safety redundancy. If the main controller fails, the limit controller will back it up.
You want to make sure that POWER LOSS to the High Limit ALSO drops out power to elements. This should answer your question about what contact to use.
Also a high limit requires reset button to reset the high limit condition (code requirement). That is why usually it is an instrument that IS a high limit instrument, not just a controller with an alarm relay.
"A high temperature limit. It is required to ensure that the maximum temperature specified by the oven or furnace manufacturer cannot be exceeded. It must require manual reset, must be of the indicating type and must be used solely for high temperature limit. (It cannot be an auxiliary contact of the temperature controller.) It must drive upscale upon thermocouple break."
The other kicker to remember...the High Limit MUST BE "FM Approved" (Factory Mutual)...... if you want insurance to cover ANY damages caused by failure of instrument..
Hello, I got a customer that has a shrink wrap machine to bundle up beer cans to make beer packs. They have a problem with the oven's all metal...
4,320
I have an oven which has a burner to burn a glass. Now it use a button to start/stop the burner. I want take off the button and connect the...
1,222
I need help troubleshooting an oven controller unit. Once in a while (not always) temp increases steadily 20 degrees above SP causing the unit to...
2,020
Hello have posted some on this earlier. have done some testing to determine best PID values but results from open loop testing were poor. any...
41
11,137
Hey Guys, I have several thermoforming ovens I am working on. These ovens have 24 heating zones. Each zone may be from 2 heaters in series, to...
1,687