fwilliams83
Member
We have a Panelview Plus 1000 communicating with a warm backup CompactLogix (L32Es with a 1769-SDN card) pair over DeviceNet. At this stage, the CompactLogix are configured to nodes 0 and 1 respectively, the HMI is configured to node 3 and there are 3 Flex IO racks set to nodes 10-12 respectively. The DeviceNet bus is currently operating at 125k.
The HMI project runs without any issues until we have to restart the program (either the panel loses power, or we go back to the configuration screen and then run the project again). At this point (probably 90% of the time) the comms don't seem to come back properly. The HMI can't write to any tags (error messages appear in the diagnostics popup) and seems limited in reading tags (most indicators show 0 although I did get an alarm which came through). However, it doesn't get any tag errors etc - it's like it's sort of communicating, but just not properly. The DeviceNet bus doesn't show any errors, and the indicator lights on the PV+ DNet module (2711P-RN10H) are all solid green, indicating that it is all working properly.
We've tried reloading the program and then running it again (replacing the comms). On startup, we have tried both replacing the comms and not replacing the comms. The only thing that seems to work is downloading the HMI program again.
Any ideas about what is causing this, and better yet, how to fix it? It's obviously not acceptable for the client to have to redownload the program everytime they want to cycle power to the panel.
Thanks
The HMI project runs without any issues until we have to restart the program (either the panel loses power, or we go back to the configuration screen and then run the project again). At this point (probably 90% of the time) the comms don't seem to come back properly. The HMI can't write to any tags (error messages appear in the diagnostics popup) and seems limited in reading tags (most indicators show 0 although I did get an alarm which came through). However, it doesn't get any tag errors etc - it's like it's sort of communicating, but just not properly. The DeviceNet bus doesn't show any errors, and the indicator lights on the PV+ DNet module (2711P-RN10H) are all solid green, indicating that it is all working properly.
We've tried reloading the program and then running it again (replacing the comms). On startup, we have tried both replacing the comms and not replacing the comms. The only thing that seems to work is downloading the HMI program again.
Any ideas about what is causing this, and better yet, how to fix it? It's obviously not acceptable for the client to have to redownload the program everytime they want to cycle power to the panel.
Thanks