Modicon Quantum with unity pro XL 2.3

gsmoh2000

Member
Join Date
Jan 2009
Location
Egypt
Posts
14
hi all

i have a problem with Modicon Quantum PLC
i have hot standby CPU 140 CPU 671 60 , it was work perfectly while doing routine check for CPU status and switching from primary to standby , both goes to run offline
try everything get new cpu cards , download the program , nothing happen and still remain
try to change the NOE cards with a new ones , also nothing happen
try to turn off power over the 2nd rack to work one primary , nothing happen
till now the problem had not been solved and i want to work even the PLC primary till this problem to be fix
what can i do?
thanks
 
Is your problem that when you make a change in the Logic on the primary cpu, the Standby changes to OFFLINE? If so, you need to set the system bit %SW60.3 to ONE to allow dissimilar programs.
 

Similar Topics

Hello all, first time poster here. I have a Quantum PLC and am trying to connect to an ABB ACS 550 Drive. We are using Modbus TCP with a RETA-01...
Replies
6
Views
6,398
Is it possible to program a Quantum Unity CPU with Concept software? Do exist a flash executive that makes it possible? Regards, Robert
Replies
3
Views
5,249
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
Replies
6
Views
261
Hi There, I have a Modicon Quantum PLC, there is a alarm on display "noConfig" its happened after power failure, I have gone through manuals...
Replies
3
Views
652
When i read the specification of 140CPU43412A i observe that as remembered in specification 1. Local i/o : Maximum i/p and o/p words are 64 in...
Replies
0
Views
496
Back
Top Bottom