Speed Speed Monitoring . ? How does it work on the drives

bornwild

Member
Join Date
May 2010
Location
Riyadh
Posts
429
Hey all,

Our have some sew movi drives. One of the drives shows fault f08 . I checked up the manual it says speed monitoring. What does it actually mean. Did i overload the drive. The drive seems to run fine when the load is less but shows f08 but some extra load is put. Also how do i increase the deceleration time . I have mt manager but when i try to change it turns dark. please help
 
I found a cut from the manual:

Wiring from VFD to motor should be of suitable size and type to
carry up to 20 amps. Wire phasing is critical for correct
operation. Wires from U,V, and W from the VFD must go to U,
V, and W on the motor along with proper grounding. If phases
are not correct, the VFD will fault on “F-08” (Drive fault 08).

Did You check the motor wiring ? What is the current load while running and set overcurrent protection limit ?

Check Page 12:
http://www.sew-eurodrive.de/s_training/teachware/pdf/WB_MDX_Stoerungsuche_Spezielle_Fehler_en.pdf
 
Last edited:

Similar Topics

Hello, I'm doing some programming for a system of conveyor belts. For some of the conveyors, there is a magnetic proximity switch counting...
Replies
14
Views
7,518
Hello everyone, thank you for your attention i have a question about Movidrive B Speed monitoring Fault 8, what exactly does Speed Monitoring is...
Replies
10
Views
9,563
Allen Bradley finally shipped my MSR57P safety relay. The relay will be wired to an existing continous web system. There are 24 motor/encoders...
Replies
0
Views
4,639
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
98
Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
Replies
2
Views
160
Back
Top Bottom