PowerFlex700 control

angi

Member
Join Date
Jan 2010
Location
us
Posts
361
Hi guys

I need to control a PF700 using CompactLogix(1769-L32E), 1769-SDN and 20-Comm Adapter. my question is how to configure the Logic Command Word and Status Word, what is the address for them in the PLC?

Thanks
 
Hi guys

I need to control a PF700 using CompactLogix(1769-L32E), 1769-SDN and 20-Comm Adapter. my question is how to configure the Logic Command Word and Status Word, what is the address for them in the PLC?

Thanks

That will depend on where you map them in the SDN Scanner. You will need RSNetworx for DeviceNet to set it all up. Appendix D of the 20-COMM-D Manual has the Command and Status Word Definitions.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/20comm-um002_-en-p.pdf

Stu....
 

Similar Topics

Hi friends. I am working on PF700, and drive is showing at speed no faults but when I am hooking up the motor, motor doesnt starts and only shows...
Replies
8
Views
1,727
I want to connect my PLC 5/40 to my Powerflex 700 trough RIO remote I/O. I am connected to the PLC trough a 1. How is the wiring in the Remote...
Replies
0
Views
1,276
We have a Power Flex 700 VFD installed which in turn gives power supply to 55 kw motor. Once the VFD tripped due to over heating of vfd. We...
Replies
7
Views
10,116
Hello, I used the powerflex 700 driver,the driver via 20-comm-e with PLC (1769-L32E) communication,I use the rslogix5000 software config the...
Replies
9
Views
2,963
Please help/advice, On Powerflex 700VC with DeviceNet communication card, the drive is off by 15 rpm at 500 RPM, at 100 RPM the actual speed is...
Replies
0
Views
1,262
Back
Top Bottom