about powerflex700 initial start up
sohelfitter07
Feb 2016
hamilton
Hi friends.
I am working on PF700, and drive is showing at speed no faults but when I am hooking up the motor, motor doesnt starts and only shows at speed. If any one knows could you guys please help me as I need ur assistance now.
Hi
Look at your speed reference as if you are requesting zero speed
Then when you start your drive zero Hz will give you at speed as that is the speed you requested
You could change the minimum speed to 10 Hz and see will your drive ramp to that Hz
Donnchadh
Thank you for your reply. You know what I connect 2 wire control and there is no fault indiciation on the display. when i am pressing start display shows at speed but 0hz is showing on the display. when i am increasing the speed from HIM its increasing and then suddenly its shows 0hz again.
Hi
Sorry I don't have a manual at the moment only using my phone
But it will be a parameter called speed source
Donnchadh
Hi
Is your motor connected in star or delta as if you have connected incorrectly the drive will not ramp up but I taught it would run at around 2 hz
Donnchadh
I want to connect my PLC 5/40 to my Powerflex 700 trough RIO remote I/O. I am connected to the PLC trough a 1. How is the wiring in the Remote...
1,278
We have a Power Flex 700 VFD installed which in turn gives power supply to 55 kw motor. Once the VFD tripped due to over heating of vfd. We...
10,121
Hello, I used the powerflex 700 driver,the driver via 20-comm-e with PLC (1769-L32E) communication,I use the rslogix5000 software config the...
2,969
Please help/advice, On Powerflex 700VC with DeviceNet communication card, the drive is off by 15 rpm at 500 RPM, at 100 RPM the actual speed is...
1,265
Hi, I have a previously used PowerFlex 700 with DeviceNet and I want to use it to run a 20HP motor powering a water line at constant pressure...
1,362