I received a call very early this Tuesday morning from the plant. A filler wouldn't go into CIP mode. Tried going on-line from home and found that RSLinx didn't see the processor. Drove to the plant and noticed that the indicator light on the power supply (1756-PA72-C) wasn't illuminated. The circuit beraker supplying it was on and there was 248 VAC present across L1 & L2, so I assumed the power supply was shot. As luck would have it, a factory technician was due that same day for PM service, so we picked up another power supply, installed it and waited for the mechanical service to be complete before turning power back on. At 3:30 PM, it became obvious that we had more serious problems...
First, there was no power to the processor (1756-L61-B). We were able to borrow one from a mothballed plywood mill, but when it was installed, we noticed the Devicenet (1756-DND) and Ethernet (1756-ENBT-A) cards didn't power up, either. After another trip to the mill, we found the Sercos (1756-M08SE) module was also bad, along with two 1756-OB16-E cards and three 1756-IB16-A cards. By this time, it was 1:00 AM on Wednesday, so we knew we were in bad shape.
Miraculously, we were able to find replacements for all the bad cards within a 4-hour drive and were up and running by midnight on Wednesday.
Although I'm pleased to be running, I'm concerned that no root cause was found for the failures and I'm hoping someone may be able to shed some light on the issue.
The filler is powered by a 575-230VAC transformer. The fact that there was 248 VAC across L1&L2 may be an issue, so we moved the primaries from 600 to 575 VAC to drop the secondary voltage.
Even though 248 seems a bit high, I'd be surprised if it caused such a catastrophic failure.
Any ideas?
First, there was no power to the processor (1756-L61-B). We were able to borrow one from a mothballed plywood mill, but when it was installed, we noticed the Devicenet (1756-DND) and Ethernet (1756-ENBT-A) cards didn't power up, either. After another trip to the mill, we found the Sercos (1756-M08SE) module was also bad, along with two 1756-OB16-E cards and three 1756-IB16-A cards. By this time, it was 1:00 AM on Wednesday, so we knew we were in bad shape.
Miraculously, we were able to find replacements for all the bad cards within a 4-hour drive and were up and running by midnight on Wednesday.
Although I'm pleased to be running, I'm concerned that no root cause was found for the failures and I'm hoping someone may be able to shed some light on the issue.
The filler is powered by a 575-230VAC transformer. The fact that there was 248 VAC across L1&L2 may be an issue, so we moved the primaries from 600 to 575 VAC to drop the secondary voltage.
Even though 248 seems a bit high, I'd be surprised if it caused such a catastrophic failure.
Any ideas?