UL safe DC voltage

Franky_B

Member
Join Date
Dec 2010
Location
Molenschot
Posts
31
Hello guys,

Question from Europe.

What's considered to be a safe DC-voltage according UL-regulations ??

Thanks in advance.

Greetz,
 
The guideline sets the upper threshold, but 24V DC is the most common DC control voltage here (same as your side of the pond) and is generally regarded as safe under most circumstances. Other common voltages are 12, 5, and +/-15 (30V span) but they are no where near as common as 24V.
 
Last edited:
in that case,

#1 - the us standard is 60 hz +/3 hz.
50 hz coils burn up in 3-6 months - from personal experience.

#2 - i would get a copy of NFPA 70 - national electric code, 70E - handbook for electrical safety in the workplace,79 - electrical standard for electerical machinery, 496 - standard for purged and pressirized enclosures for electrical equipment.

depending on your requirements, other standards may also apply.

regards,
james
 
NFPA 70 is the regulatory code. UL is not a regulatory authority, it is an approval and certification agency. Local jurisdictions have authority over code adoption and enforcement but they universally adopt NFPA70 and occasionally augment it but very rarely countermand it.

NFPA 79 is a subset of NFPA 70 that pertains to industrial machinery and I strongly recommend getting a copy and using it. Google NFPA 79 to find dealers. NFPA 79-2012 is the current version. I think that the 2007 version of NFPA79 is now available as a free PDF and that should help you a lot to get you to where you need to be.

We sometimes ship machinery to Europe and sometimes import machinery from Europe. From my experience the biggest hurdle is going to be the 50/60hz frequency difference, and even that is not a big deal. Motors will rotate faster on 60hz and draw slightly less current. Transformers are a little more efficient at 60hz so secondary voltage will be slightly higher. Avoid using 230V control voltages - while 230V systems are common, it is not a common control voltage and replacement parts may be difficult for customers.

Fuses - Euro bottle style fuses are not common here and are difficult to find. On the other hand, 5x20mm fuses are very common.

Breakers - Some Euro din rail mount breakers do not meet code for primary branch circuit protection (not robust enough) and are only suitable for use as supplemental protectors. Look for UL489 markings on din rail mount breakers used as primary branch circuit protection.

Wire sizes: Always convert up in cross section and down in current rating. For example, 12 gauge wire has a cross section of 3.31mm2 and is rated at 20 amps. You will have to convert up to 4mm2 wire, which is bigger, but still protect the wire at 20 amps as though it was a #12 wire. You'll find that some wires sizes favor the IEC ratings while some favor the NEC ratings.
 
Last edited:

Similar Topics

I've seen 24VDC on these "Continuity" type switches before from multiple OEMs. You connect 24VDC to the Common of a Sourcing Input module and...
Replies
11
Views
3,975
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
199
Can somebody share the AutroSafe configuration Tool C4.11.4 Thank you
Replies
1
Views
135
I have a GuardLogix PLC with safety inputs of HMI, Estops, Light Curtains, and Gates. Is it considered safe for the safety program to monitor the...
Replies
11
Views
810
Back
Top Bottom