Can't establish basic USB comm with Data Station Plus

danw

Lifetime Supporting Member
Join Date
Oct 2004
Location
midwest, USA
Posts
3,429
Problem: Can't download a basic comm configuration to DSP

Error: Target Device is not compatible with this file

Red Lion Data Station Plus (DSP), model DSPSX000 (no CF card)
Software: Crimson 3.0 build 443

goal: Set DSP up as Modbus/TCP master, read from device B, write to device A

2lw9c1g.jpg

1) set up comm between Crimson and DSP:
Link > Options > Comm port = USB. USB cable plugged in on both ends

Communications > Programming Port = no driver selected

2) Configure IP address for DSP
Network > ethernet 1 > port mode = manual config
IP address = 192.168.1.90
mask = 255.255.255.0

2a9bo6q.jpg


3) Define protocol for DSP
Protocol 1 = Modbus TCP/IP master

4) Configure IP address for device A
Network > Protocol > PLC 1 > IP = 192.168.1.85
33jtpnl.jpg


5) Configure IP address for device B
Network > Protocol > PLC 2 > IP = 192.168.1.62
2hxwupu.jpg


Attempt to download to DSP:
Link > Update > Target Device not Compatible
2i71d15.jpg


Any action from Link fails with the same error.

What am I missing?
 
Last edited:
Do Link Extract and see if the device will tell you exactly what it is.

I wonder if you may need to download an old rev. to get firmware updated or if it's not compatible with Crimson 3.0
 
It's new, and the date code is 3311x (33rd week of 2011)

The way I read the compatability table (from the web site above), the DSPSX is C3 (Crimson 3) compatible.
f59860.jpg
 
Your screen shot shows that you are trying to download a configuration for a G306. Please go to File > New and choose DSPSX.

Thanks
Jeremy
 

Similar Topics

I have Bailey infi 90 DCS system The composer (EWS) was unable to establish communication with ICI . I got this error message anyone has any...
Replies
0
Views
491
Hey all, I am experiencing issues activating some rockwell products. I have submitted a ticket to rockwell with request for assistance, but to be...
Replies
19
Views
3,238
Good day Programmers I have a RSTi-EP CPE100 Standalone Controller from Emerson as well as a STXMBE001 (MODBUS TCP/IP) as a Modbus communication...
Replies
0
Views
668
Hi All, We are using M580 Level 4 Hot Standby System. We are using the BMENOC0301 module to do Modbus scanning from the Modbus units (Genset...
Replies
5
Views
2,332
Hi. I have a PanelView Plus 600 panel and a Honeywell C200 controller. The task is to connect them for joint work. FTView Studio 6.10 software is...
Replies
4
Views
2,398
Back
Top Bottom