hello.

suppose that i have a s7-300 plc with cpu315 which has a mc card and battery.there is an op17 that values of op transferred to retentive db on cpu.

will all data on mc be erased if the battery became disconnected?

what does happen on value of db and op if i download the earlier backup file to the plc?

i have a cpu with part number 315-2af01-0ab0.are data blocks in this cpu retentive?

best regards.
 
hello.

suppose that i have a s7-300 plc with cpu315 which has a mc card and battery.there is an op17 that values of op transferred to retentive db on cpu.

will all data on mc be erased if the battery became disconnected?

Not if the power (24V) is on.



what does happen on value of db and op if i download the earlier backup file to the plc?

You will get the old values from the backup.
If you have the gear to download, why not do an upload imediately?


i have a cpu with part number 315-2af01-0ab0.are data blocks in this cpu retentive?

The DB's values survive a restart of the CPU. Still it might be done a programmed (p)reset in the startup OBs.

Kalle
 
thanks a lot for your reply.

please excuse me because my english isn't good. are you mean that value of dbs will not be erased after power down of cpu?

are db values saved in mc card?

if i turn off cpu(remove 24v) and pull out the battery the data saved
in mc card will be erased or not?
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
6
Views
128
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
Replies
5
Views
177
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
36
Hi All, Someone at work has put a PLC system on my desk, that's just been taken off an idle production line. He said "It's an S7 PLC. We don't...
Replies
10
Views
247
I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
64
Back
Top Bottom