Dears
I was making online modification in such CPU when i was in remote program mode starting to edit rungs as per manual
edit rung
modifiy
accept the rung

but i found that after this step the controller fix some output without any change as ex. keep the valve open and not excuting program to close knowing that the block which i was modifing has no relation with this output which is freezed to open


is any one has experience with such situation and why it happened

thanks in advance
 
here it again
i was making online modification for some rungs, the steps was:
i went to remote program ( run led was off)
edit the rung
accept the rung
but what happen is when the new rung is going to be excuted i found that one (input) from the rung which i edited is going to one and freezed this is what i noticed may be many gone to freeze
is there is a reason for this ?:unsure:

i hope it is clear
 
actualy i start modification by REMOTE program mode
and i was going to edit one rung
after edit
accept pending rung edit
then no need to assemble because i was in program mode not run mode
before returning the mode to run this problem happened
 
When you do edits online you have to accept the pending edits, this then tests the edits but does not execute the edits.

Then you have to test the accepted edits, which means the program is now running those edits.

Then finally you assemble the edits.

If you edit in program mode then you have to put the program back into run mode.

Mark
 
When you do edits online you have to accept the pending edits, this then tests the edits but does not execute the edits.

Then you have to test the accepted edits, which means the program is now running those edits.

Then finally you assemble the edits.

If you edit in program mode then you have to put the program back into run mode.

Mark
In which version of RSLogix5000 are you working?
I'm working in V19 and can edit directly with one button...
 
Dears
My version is V16 and i make many modification before with the same mode remote program
and sure after excuting the modification i have to return back to run mode but this problem happened before going back to run mode
and after i edited i did accept the edit rung and this step include also the rung verification.
sure the rung which i did is corrct brcause i left it in the programe after this problem without any problem
 
actualy i start modification by REMOTE program mode
and i was going to edit one rung
after edit
accept pending rung edit
then no need to assemble because i was in program mode not run mode
before returning the mode to run this problem happened


On a side note, I really caution against your approach on this. Since you are working only "online" I assume that you don't have a commented version of the program. If this is so it is very important to upload the progam and state of the controller, and back it up to a separate file name before making any changes.

It sounds to me that the last guy may have had forces enabled, and what you did lost those forces.
 
I'd be willing to bet (much more than pocket change) that what you saw was actually the RSLogix5000 software "freezing" instead of the PLC ...

it's a fairly common occurrence to have the software do weird things – as shown in the picture below ... this was something that happened to a student in one of my classes a few months ago – and I was able to capture a screen shot of it ... we had to stop and then restart the software to clear up the problem – and the same situation has never happened again ... this was version 16 of the RSLogix5000 software ...

notice that the CTU and the CTD instructions both have exactly the same address ... that means that there is only one Accumulator involved ... so theoretically the value shown for the Accumulator in the CTU instruction should always match the value shown for the Accumulator in the CTD – and it should also match the value shown for the Accumulator being shown in the Tag Listing ... obviously that didn't happen ...

going further ...

as the input switch (bit 2) controlling the CTU was toggled OFF and ON, the Accumulator value shown in the CTU instruction stayed "frozen" at ZERO - and it would not count up ... at the same time, the Accumulator shown in the CTD instruction did indeed "count" – but it was actually counting UP instead of DOWN ...

note that the value for the Accumulator as shown in the Tag Listing did indeed accurately increment upward each time the switch for the CTU instruction (bit 2) was toggled ON ...

to the student, it looked like the input switch was controlling the wrong "counter" – and that the CTD instruction was "counting Up instead of DOWN" ...

but ...

when you get right down to the key facts, the value displayed for the Accumulator in the CTU instruction stayed "frozen" and would not update on the screen ... everything else was actually working correctly ...

in other words, the PLC was NOT "frozen" in any way - it was only the SOFTWARE that was hung up and not displaying the PLC's status correctly ...

we finally had to stop and then restart the software in order to clear up the display problem ...

so ...

as I said earlier, I'll bet that the problem that you saw was actually the RSLogix5000 software display "freezing" – instead of the PLC ... if it happens again, try to capture a screen shot of what you're seeing ... that might help us nail down your problem ...

.

ctu_not_ctd_2.jpg
 
Last edited:

Similar Topics

I am trying to set up a read message in a MicroLogix1100 to read the value of a DINT in a ControlLogix5561. I have successfully set up a message...
Replies
2
Views
190
Hi to all, We had a machine down with a bad RsLogix 5000 processor. There is a red light on the processor for ok. The bad processor is a Logix...
Replies
3
Views
1,778
I use Rslogix5000 Enterprice and my old control logix 5561 Catalog\Series 1756-L61 B is damage, and i change it by new one after that i download...
Replies
4
Views
1,805
Hi, guys, how’s going? Two weeks ago, after a power outage, Logix5561 lost the program, so we had to download the program to the controller...
Replies
4
Views
2,942
We have a Controllogix based process line with a PC based HMI, held proprietary by the equipment manufacturer - Ethernet communication. What I...
Replies
3
Views
2,383
Back
Top Bottom