To Message data between two CompactLogix controllers, Do you setup a MSG instruction to do a CIP write in the Master and setup a MSG instruction to do a CIP read in the Slave? Or does using the MSG instruction to do a CIP write push the data directly into the destination tag on the Slave?
 
You can do either a CIP Write or CIP Read. I always use a read. That way you can always figure out where a tags' value is coming from. Unless documented very well, MSG writes can cause confusion as to where a value is coming from and how.
 
But you only need to do one or the other, either a Write or a Read. You do not need a write in one controller and a read in the other for the same data. Is my thinking correct?
 
I cannot believe that no one has posted use produced/consumed tags instead.
This would be what I would be looking at doing, unless you only want to msg at slow intervals..
 
I cannot believe that no one has posted use produced/consumed tags instead.
This would be what I would be looking at doing, unless you only want to msg at slow intervals..

Yes, that is one way to do it for sure. But for some reason that does not work over radio networks. I have no idea why.
 
Well that make it a different kettle of fish then..
Are they Ethernet Radios? I suspect there is too much latency in them to perform the throughput required for Produced/Consumed.

Maybe this should of been mentioned first...?:oops:
 

Similar Topics

Good morning, I’m looking for assistance on what hardware is needed to message from a CompactLogix L3 controller to a SLC 5/03 or 5/04 via serial...
Replies
2
Views
1,321
I am trying to read a block of data from an ML-1400. The data is in the form of floating-point numbers. I am only able to read only 59 numbers...
Replies
2
Views
1,201
Good Evening , I'm sorry. so many PLC concepts I still struggle with. I need to move some 8 digit numbers from a SLC 500 5/05 processor to a...
Replies
12
Views
3,722
Hi,* New to the site. I am trying to meassge between a Compactlogix 1769-L18ER-B1BB and a Micrologix 1400. I am using Studio 5000 V24. I can...
Replies
2
Views
1,791
Good Morning , We are getting ready to do a small project with a Cognex Vision System. We have a SLC 500 , controlling the operation , but...
Replies
5
Views
1,448
Back
Top Bottom