m340 plc

mpppandi

Member
Join Date
Feb 2011
Location
*******
Posts
8
hi, i am using m340 plc. i am not able to assign float data type to symbol, i am using bmx p342020 cpu,, whether its possible in that one,, if anybody know tell me
 
Yes - floating point is supported
Go to the variable table, select the tag then in the type column use the dropdown box and select REAL
 
first thanks for reply ,, you are telling ok but when i put address %MDn to the floating type ,, it is not supporting ,, how can i solve it,, and i read through help menu,, it is telling that is not available for %MDn to the m340 plc,, then how to solve it,,
 
You have to use %MW address for reals and double words on Unity software. PLC uses two %MW addresses for one real variable.


varible1 real %MW100
variabl2 real %MW102
...
 
thanks lare ,, yes you are telling correct,, thats i got from my friend, but next time i will ask complicated questions to you,,
 

Similar Topics

Good day, I have an issue between an M340 PLC and a PRA 0100. The problem is as follows: I have a communication link between the PLC and the PRA...
Replies
0
Views
830
Hello, Not able to find Modicon DO modules BMXDDO3202 in EcoStructure Control expert V15 catalogue. But i can find only MBXDDO3202K. Can you...
Replies
2
Views
467
so i have an isssue where if the serial port of an M340 plc disconnect from the screen it would retain the values of the variables being sent...
Replies
1
Views
914
I need to establish communication between Schneider M340 and S7-1500 PLC. I am using gateway converter for MODBUS TCP TO PROFINET protocol...
Replies
12
Views
2,985
hello i want to read temperature data from Masibus UT94 temperature transmitter which is giving data on RS485 port. i have assigned ID:-30 and...
Replies
1
Views
1,059
Back
Top Bottom