Trying to reference an output from a Micrologix 1100 on a PanelView Component C600...

For the base PLC outputs it works fine to just address the outputs in the HMI as O0:0/0. Yet, for the outputs on my output card, addressing the outputs as O0:1/0 doesn't work. The HMI doesn't seem to recognize the output card outputs. I quickly tried O1:0/0 and O1:1/0 but those don't seem to work either. Any ideas?

Thanks in advance.
 
The easy way to do it is to copy the data into a B or N file and read it from there.

If you absolutely must access it directly, RA Knowledgebase article 67770 (TechConnect Access) explains the unusual offset values you need to use when addressing MicroLogix expansion I/O from the PVc.

The PanelView Component doesn't use "slot" addressing, but rather only "offset" addressing, and the Expansion I/O is considered offset by +1 word.

The MicroLogix 1100's built-in Outputs take up Words 0 through 5.

Try addressing the first Output card as Slot 7, like "O:7.0-15".
 
Check your I/O Configuration check your card's allocation.these plc's allow for o0:0/18 or o1:0/2
the compact HMI also is not that friendly - stick with "B3" Or "Bx" to display output status

like Ken said
 

Similar Topics

I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
241
Hi, I have an issue accessing tags in 3 of my plcs'. When I go to select a tag there is no folder drop down as can be seen in the photo. Any...
Replies
0
Views
104
Hello all. I have a feeling I am going to shame myself with this question but I can't resolve it and can't figure it out......probably making it...
Replies
13
Views
1,067
I have not used Logix beyond V24 for a few years (production environment) until recently. I have 3x L84ES in a new project. We are sending...
Replies
1
Views
811
Hi All, I have a new 5 PLC system. Each has the same firmware revision. Each PLC has the same User Defined UDT for Safety Tags. PLC1 reads from...
Replies
2
Views
2,022
Back
Top Bottom