micromaster 440 inhibited

Many thanks for your reply ! I am VERY new to this and I do not have a software engineer on site ! How do i set that bit you mentioned ? Bit zero of the first control word is ON ( i can see that using STARTER software. All the other VSD's that bit is OFF ).
 
We need more info here.

A: Is it already a program in a PLC running this MM4?
B: What type of PLC?
C: Has it worked before?

So, if you've got a Simatic 3/400, you'll see how the bits are set on a running MM4 (from Monitor/Modify) if you check the link I just posted.

Kalle
(edit: sorry for that stupid icon. Not intended, old shaking fingers, sensible touchpad.)
 
Last edited:
Its a 318 PLC.When i push start on the HMI i can see 5% going to the drive and the brake comes off ok. Never has worked before, we are at the commissioning stage. If i control it from an AOP it works fine in both directions. Will have a look at your link thanks.
 

Similar Topics

My tutor asked me for this small project: using S7-200 control MM440 with PROFIBUS. Because S7-200 with PROFIBUS module EM277 can only be PROFIBUS...
Replies
4
Views
3,000
fault A0501 (i.e current limit ) displaying whwn i replace siemens 420 drive with mm440. all parameters are crosschecked. please help to...
Replies
4
Views
1,578
I have a Siemens Micromaster 440 (6SE6440-2UC25-5CA1) with encoder module (6SE6400-0EN00-0AA0) and Profibus module (6SE6400-1PB00-0AA0). I'm...
Replies
1
Views
3,081
Hi All I have the SIEMINS micromaster 440 not starting good several times then start after 1 to 2 hours . so I took the AOP kit and opend it >>...
Replies
12
Views
4,483
Dear all, We are working with MM440 at th plant where i'm working. The MM440 is connected to S7 400 PLC. In the hw config the setting is 0PKW...
Replies
2
Views
1,443