SEW Inverter

Japaunks

Member
Join Date
Jan 2012
Location
Jeddah
Posts
8
Hi, Im new here. I want to use a SEW Inverter as a drive for my Siemens PLC thru profibus interface. Do you have a program with start stop operation for this.

Thank you!
 
you will need to give much more info for us to answer.
The Profibus i/face is the control for the drive - so after setting it up you need to send data from the siemens PLC.
contact SEW-EuroDrive for wiring of the drive.
 
What I mean is if you have a sample S7 program with start and stop operation using SEW as inverter for a motor. I dont know what function block to use. I have the GSD files with me.

Thank you!
 
There is no special block to be used.
Just plonk in the inverter in the HWconfig, make the correct settings and reference the inverter by using the correct PIW and PQW.
To find out which bits need to be TRUE and which ones need to be FALSE, it's best to visit the SEW Eurodrive site.
They have a few example projects for S7 and all the information you need.
 

Similar Topics

What does the 24V operation of sew inverter mean? I can't make the inverter starting the motor
Replies
2
Views
469
Technologies: Tia 15.1 update 5 Siemens CPU 1517F-3 SEW MDX61B+DFS21B From the TIA hardware configuration, the SEW drive is accessible from...
Replies
3
Views
1,752
Hello, I have not programed plc wtih profibus communication yet, so If anybody has any idea how to please help. So I use PLC CX2020 and program...
Replies
5
Views
2,363
I'm having a SEW Drive Inverter fault code: F14 which is a Encoder fault. The subcode that I have on movitools is the 27 Encoder error - encoder...
Replies
10
Views
10,676
Dear colleauges,we have got a S7-300 plc and a SEW Inverter .Now there is a problem.When we give start to system firstly break enable signal come...
Replies
1
Views
3,995
Back
Top Bottom