I have not programed plc wtih profibus communication yet, so If anybody has any idea how to please help.
So I use PLC CX2020 and program in TwinCAT 3. I want to Control SEW MOVIDRIVE Inverter through Profibus.
How can I read, write from slaves and run/stop Motor connected to Inverter?
I so a lot ex. in Tia Portal with S7, but I have another Equipment.
Thank you.
Hello,
I use EL6731 Master/Slave terminal for Profibus.
I have read menual for SEW MDX61B0055 Inverter. I set Parameters that needs to be set (100 and 101 fieldbus, 870-875 for PI and PO ans 876 enable YES) on keypad.
I still can not Control from PLC.. Only manually.
Hello guys!
I solved this a while ago and remembered that I can wrote a solution for others..
So my problem was that I could not control SEW motor through inverter that was connected to PLC through profibus...
Then I figured out that my Status Word is not good..
That was because Profibus is by Siemens, PLC is by Beckhoff and Low and High Byte needs to be swapped in that case.. So I that case click on every input and output you made for inverted and open Flags, then fill Swam LOBYTE and HIBYTE...
Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
348
Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
790
Hi, I have a doubt about the system architecture shows below: could two master devices install in same profibus network?
2,657
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
2,836
Dear superiors, When i try to communicate Yasakawa A1000 AC Drive and simense s7-300 plc via profibus the drive shows error bb on its display...
6,920