PLC, Remote IO and HMI in same Profibus Network
xcyong89
Oct 2019
Kuala Lumpur
I have a doubt about the system architecture shows below:
could two master devices install in same profibus network?
It is possible. If it is a siemens HMI, then you can setup routing between the HMI and the PLC CPU.
Is this an upgrade of an existing system from S7-300 to S7-1500, and then keeping existing ET200M racks on profibus ?
If so, a smarter simpler way would be to exhange the Profibus IM153-1 in the ET200M racks for Profinet IM153-4.
Unless the HMI is ancient, there is usually ethernet on board besides Profibus.
thanks a lot for the feedback.
Yes, this is a upgrade task of existing system from S7-300 to S7-1500 and keep existing ET200M racks and existing HMI (Siemens WinCC Flexible without Ethernet port) on profibus.
kindly find the existing architecture below:
In this case, does the design of Profinet IM153-4 is suitable for this task?
If everything is Siemens everything should be taken care of automatically from a configuration point of view. You need to take care of station numbers and network parameters. The HMI is a master class II device, the PLC is a master class I device and the remote IO is a passive device. Normally station 1 for the PLC, station 2 for the HMI and higher station numbers for the remote IO. Last active station should be at least the same as the HMI, in this example, 2.
Siemens S7/TIA v18: "Remote" updates/bug fixes to PLC code & HMI screens..... Hi, The PLC application I'm working on will soon be delivered to...
580
Hi all, What is everybody using for getting access to remote machines PLC/HMI local network for snagging and debugging from their desk ? We...
21
9,861
Hi All, We are looking at installing remote access for a client so that we can log-in remotely and troubleshoot the PLC but also so that the...
2,614
I have a panel in front of the equipment with a PanelViewPlus 7 standard with Factory Talk ME and a Factory Talk SE HMI up in the control room...
2,130
Hi All, I'm looking for a PLC and HMI for a small brewery to monitor fermenter temperatures and adjust setpoints. The part I'm struggling with is...
3,549