i'm looking for opinions on which output to send to the analog out module when using a PIDE. it appears CV is 0-100 so i would have to use a MUL to scale the CV to match the output module range. on the other hand, if i use CVEU, i could make it match the output module range. the problem is that i am going to have some manual settings that go to a on the HMI to set the valve at 0-100, i guess i would have to multiply that too then. Would it be easier to use the CV and make 1 final MUL that ranges it to the output module? Am i barking up the wrong tree?
 
Use CVEU. Your manual settings should go into the CVOper or CVProg inputs on the PIDE instruction. The inputs would be in percent and the instruction will scale the CVEU output for the module.
 

Similar Topics

I am working on a project where I need to create a visualization screen (HMI Panel or PC) using wincc tia portal v16. It will be connected to the...
Replies
3
Views
533
Are there any HMIs besides C-More that offer a driver for the Automation Direct Productivity series PLCs? Running into some issues with C-More and...
Replies
10
Views
1,530
Got an old machine with a IC610CPU104 CPU. A bit of research told me this is the same as DL305 so DirectSoft from AutomationDirect should work...
Replies
15
Views
2,041
I need some clarifications from VFD experts. I have a project with a vibratory conveyor that must be stopped relatively quickly. Stopping is once...
Replies
2
Views
788
Hello all. I have a parts elevator in a very dirty environment. I have used VFD's a lot over the years but I have never had to have one with a...
Replies
11
Views
1,777
Back
Top Bottom