Sending and recieving sma using PLC

eababio

Member
Join Date
Jan 2011
Location
Gaborone
Posts
52
Hi All,
Has anyone worked o a project with a master plc and other remote plc that talk to each other using sms and or GPRS and sms as backup? which are the best products for this.

Will can micrologix do this? and if so which modem has worked with it?
 
Hi,

Never done that exactly, but similar.

Take a look at the 2 x PDF's (via links below) - they are fairly old, but outline what you are trying to achieve. This is a Siemens solution, but the principle is the same for most of these small brick PLC's + a modem...

We have done several projects with Micrologix using SMS so you should be able to implement the same concept as detailed in the Siemens documents.

http://db.tt/NuyS26nA

http://db.tt/wKZIuLCs


Hope this helps.

Rob
 
Hi,

We have used a range of AB controllers including ML11/12/14/1500 and Siemens S7-200 with a modems such as Westermo and Siemens...

Most of these devices support pretty much the same instruction set and there's normally some way of achieving what you're trying to do.

Without knowing your exact application, you may need to consider the reliability of your proposed setup. GSM/GPRS are obviously not 100% guaranteed, but if all you intend is a bit of remote indication or the like, then should be fine (would hate to think that a complete control system is sat in a critical condition waiting for a text message!!) :whistle:

Hope this helps.

Rob
 
we are just collecting elavated tank levels at remote sites and starting and stopping pumps from control centre plc depending on levels at the reservoir which will be at the control centre. RF is expensive as the terrain is not even and we talking of 2 remote sits at distances over 6okm. The only realistic option is GSM/GPRS for now.GPRS might not be stable and will be expensive so i need to be sure GSM can be a back up solution as well.
 
I did a remote messaging setup with WIN911 a while back. I can't remember the modem that I used. It was a ControlLogix/View SE project. You might get in touch with the guys from WIN911. They will at least be a good source of information.
 

Similar Topics

I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
83
Hi I need to send a null command down a comms port. But in the crimson software when i used /x00 it coming back "Cannot use null character is...
Replies
2
Views
420
I've been having some trouble figuring out how to get the ip address for the mail relay server, is it something that I need to create separately...
Replies
10
Views
912
Hi Everyone, We have Silo System which has temperature sensor and these sensor data will be communicating through RTU unit to the Dedicated PC...
Replies
2
Views
615
I've been trying to get this Ethernet module configured to send emails to our relay server but cannot get it to work. the EN2T is running...
Replies
7
Views
1,761
Back
Top Bottom