Hey guys,

I'm having some trouble getting my Micrologix 1200 setup with a 1762-IF2OF2 analog input/output card. I am trying to use it to read analog voltage (0-10) from a pressure transducer. I have the DIP switches set for voltage, as well as the card is set for voltage in RS500.

I checked the sensor, connected directly to a DMM, and it checks out fine. But when I have it connected to the PLC I read nothing across the terminals and get nothing but interferance in RS500. I believe I have it wired properly according to the manual.
I've tried everything I can think of and I'm all out of ideas. Can you guys think of anything I've overlooked?
 
I believe I have it wired properly according to the manual.

It sounds like a wiring issue to me. But sense we can't see how you wired it can you provide a drawing of how you wired it? ( or picture). Terminals for the input's + and -
are on opposite sides of the module. Please forgive me if that is a little to obvious, sometimes it's the little things.
 
So I hooked up my scope, and saw some really funky stuff going on. Replaced some of the wiring on my DC bus, problem solved. Strange indeed. Guess I had a loose wire somewhere. Even though I could read my 24v across the sensor power wires.
 

Similar Topics

I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
Replies
3
Views
671
So I've got a 1762-L40bwar Micrologix 1200 PLC. I'm looking to incorporate atleast 2 analog sensors into my project (conductivity and pH) and I am...
Replies
4
Views
2,647
I know this is probably simple but I have never tried before. I have a Maple touch screen HMI connected to a micrologic 1200 plc. I am trying to...
Replies
14
Views
11,186
Hi Guys/Gals I am having a problem connecting a pressure transducer to an analog module. This my setup; Pressure Transducer Thyracont...
Replies
10
Views
9,478
I have a 4-20ma signal coming from a scale unit into one of my analog cards that has some horrible fluctuation on it. I am using the scp...
Replies
4
Views
5,498
Back
Top Bottom