Can someone help me i am trying to set up a ctrio module on a dl 06 when I go into the workbench I get a "error reading shared ram" message. Everything I checked so far seems ok.
 
I assume you've already done what the FAQ suggests?

"Error reading Shared RAM!"
This means that the CTRIO cannot read/write to the PLC across the backplane. This is commonly caused by one of the following:

- You are trying to connect to a CTRIO via DCM, ECOM or serial connection and you have selected DirectNET protocol. You must use K-sequence protocol. Or for the ECOM you can also use ECOM protocol (recommended).
- You are trying to connect to a CTRIO that is installed in a PLC rack whose CPU has a password and it has not been unlocked by DirectSOFT. To fix you must connect with DirectSOFT and enter the password.
- Try reseating the CTRIO or trying a different slot.
- The slot, backplane, CPU or CTRIO is defective. Replace.

🍻

-Eric
 

Similar Topics

Hi, I am trying to learn how to use my encoder with my PLC. I recently got a high-speed counter module (H0-CTRIO2) for my DirectLogic05 PLC. I...
Replies
5
Views
2,214
Hi there, I have a vision project on that has been through some pretty major paradigm shifts since its inception. Without getting into too many...
Replies
5
Views
3,995
Hello all, I have come up against an issue trying to run a stepper motor using an Automation Direct H2-CTRIO2 module. Simply speaking, my setup is...
Replies
0
Views
2,682
Have an automation direct dl-260 cpu, and the above counting card. Have taken the signal from an existing encoder (1000 ppr) with only one signal...
Replies
1
Views
1,822
Hi, I am a complete newbie when it comes to PLC programming and would love some help. I am trying to configure a machine consisting of a DL-06 plc...
Replies
2
Views
1,661
Back
Top Bottom