93lt1
Member
Is it possible to do program upload/download across SLC channels 0 and 1?
My idea of bridging DH+ and DH-485 networks (via AIC+ connected to CH0 of the SLC)isnt possible?and to a lesser extent will bridge messages from DH485 to DH+ (I've not been able to do upload/download/online that way).
The default setting for this bit is clear (0). When clear (0) the processor allows packets to be passed from one channel to the other. When set (1) this pass-thru is not allowed. Channel 0 must be configured for DH-485 protocol. Only packets that contain the Internet network layer and whose Destination Link ID equals that specified for the opposite channel will be passed. The default Link ID for channel 0 is (1). The default Link ID for channel 1 is (2).
Ken Roach said:Well, this has the makings of a Long Story....
You've seen that the SLC-5/04 can bridge DH+ to DH485 pretty effectively. You can't talk to some older devices on DH-485 over this bridge because of their limitations in responding to off-link messages... so your 5/02 is out of luck.
But but but...
You can send & receive messages from the 5/02 etc if the message is initiated from the 5/04.
We have an application where data to/from a DH+ Panelview goes to a 5/04 slc, then onto a fixed I/O slc500 on a DH485 network.
(I'll admit we cannot download/upload using this bridge, but sending messages has been ok. We actually use a KA5 card that resides in a PLC 5 rack for this purpose.)