HarleyHetz
Member
Hey guys,
First post here, we are attempting to upgrade a PLC5/40 to CLogix. Converted the program by hand, used addressing scheme that we have used several times before where we don't have to change wire numbers, simply alias everything so techs don't get anymore confused than they already are!!
Problem with this one is that the PLC5 has 16 point cards, everything else we've done had 8 point cards!! This was much simpler because all of the "groups" would line up with the I/O that was automatically created in the CLogix processor.
The PLC5 has a 12 slot rack, and is using 1 Slot addressing. PLC is in slot 0 and will be changed to an RIO card. Slots 1-4 have 16 point input cards, and slots 5 - 8 have 16 point output cards. So, the confusion comes when we are trying to figure out how to point to PLC5 address O:010/00 - O:010/17 in CLogix. We run out of addresses, even when we tell CLogix that there is a Full Rack connected to the RIO card!!
Do we just need to add another rack to the CLogix configuration, or do we need to actually install another PLC5 rack and then add that to the configuration???
Thanks in advance for any assistance!! I can post the offending programs if that'd help...
First post here, we are attempting to upgrade a PLC5/40 to CLogix. Converted the program by hand, used addressing scheme that we have used several times before where we don't have to change wire numbers, simply alias everything so techs don't get anymore confused than they already are!!
Problem with this one is that the PLC5 has 16 point cards, everything else we've done had 8 point cards!! This was much simpler because all of the "groups" would line up with the I/O that was automatically created in the CLogix processor.
The PLC5 has a 12 slot rack, and is using 1 Slot addressing. PLC is in slot 0 and will be changed to an RIO card. Slots 1-4 have 16 point input cards, and slots 5 - 8 have 16 point output cards. So, the confusion comes when we are trying to figure out how to point to PLC5 address O:010/00 - O:010/17 in CLogix. We run out of addresses, even when we tell CLogix that there is a Full Rack connected to the RIO card!!
Do we just need to add another rack to the CLogix configuration, or do we need to actually install another PLC5 rack and then add that to the configuration???
Thanks in advance for any assistance!! I can post the offending programs if that'd help...