Do some of you know exactly when we need to add an intrinsec barrier in a CL1 div 2 panel and when we don't.

I use to install them for my 4-20mA loop and for my on/off but i bet in some case i'm over designing it and lose some jobs

i have an actual application to retrofit where i would need to connect a CL1 div2 plc to a 4-20mA transmitter with internal isolation but not rated cl1 div2
The plc is in a cl1 div2 zone where the transmitter is in a safe zone...
 
Zone classifications

As far as i know you would use the barrier when your cabinet is in a safe zone and the instrument is in a hazardous area.


As for panels that are within a hazardous area the barrier would not be effective you would need a different explosion prevention techinque. In this case i would say purging the panel with nitrogen. Obviously the panel would need to be sealed properly to accomodate this.
Here is a link to other posts on this site.

http://www.plctalk.net/qanda/showthread.php?t=17671

Hope this helps
R
 
Last edited:

Similar Topics

Hello all, This is my first foray into intrinsic safety, but I feel like I designed a solid system. Inside the hazardous area, the only...
Replies
13
Views
3,416
Hello, I have a client who has recently decided to retrofit an existing machine to ensure intrinsic safety. I have very limited experience with...
Replies
9
Views
2,559
Can I install receptacles that contain only intrinsically safe circuit conductors in a Class 1, Div 1 Area for connection to a cart that has...
Replies
6
Views
3,153
Dear, i am looking for a reference or standard stating that an intrinsic safety earth bar is required, i guess it should be seperate from the...
Replies
1
Views
1,845
Do I need to put intrinsic barriers on instruments that are rated Class Div 2 and non-incendive? The mass flow controller tech support person...
Replies
9
Views
3,381
Back
Top Bottom