How do you configure a Alarm for a RSLinx Enterprise Device losing communication? Using ML 1400's just need a bit to monitor for a communicatin loss... Seems like it would be a simple thing but havn't found in any of the Rockwell Literature
 
Look in the diagnostics folder under your shortcut folder when you browse for tags. There's many tags there you could use for that status.
 
I have tried several of the @tags in the diagnostic folder. They all seem to be related to the PLC status not the link status..
 
I'm missing something here... It is a string value. If display it on a screen it wireframes like every other object. How do you alarm on a string?
 
You can create a derived tag and then use an expression: If @status = 'OK' then 0 else 1 for example.
 
I couldn't make that work but it got me to a point where I found something that would... If comm_err({[Plant_Lift]@Status}) Then 0 Else 1 Thanks for the help
 

Similar Topics

As in add a device that is not listed on the drop down menu. For example a micrologix 1500 does not appear as an option in the Add Device...
Replies
9
Views
4,104
I don't have a whole lot of experience with RSLinx Enterprise or I guess it's also called FactoryTalk Linx. We have a Rockwell FTView SE based...
Replies
0
Views
37
Hi All, Looking for some clarity regards the relatively recent rebranding of RSLinx Classic. From what I can make out from the RA website and...
Replies
9
Views
2,509
Besides a $3,000 license to purchase a RsLinx Gateway License for every remote computer network that I work on. Is there another way to get to a...
Replies
4
Views
2,716
Hi, I'm running FTView v9 on a VM machine. Host win 10 64 bit, virtual win 7 pro. I've come to configure communication on this project (1st...
Replies
2
Views
2,180
Back
Top Bottom